Threadinq
Closed SDVOSBC

J047--FY26 NRM -Medical Gas Deficiency 610A4-26-507 (VA-26-00058207)

Agency
VETERANS AFFAIRS, DEPARTMENT OF
NAICS
238220
Place of performance
Fort Wayne, IN
Closed
Jul 29, 2026
Posted
Jun 11, 2026

Description

SCOPE A recent medical gas evaluation identified deficiencies on the 3rd Floor. The Contractor shall correct all cited items and ensure all O (OXYGEN), MA (COMPRESS MEDICAL AIR), VAC (MEDICAL VACUUM), WAGD (Waste Anesthetic Gas Disposal), N (Nitrogen), N O (Nitrous Oxide), valves, alarms, and infrastructure are fully code compliant and fully operational. Code Compliance Requirements All work shall be performed in accordance with NFPA 99, 2018 Edition. Any location where N O or halogenated anesthetic agents may be administered - including CT, X-ray, and imaging rooms using roll in anesthesia machines - shall be equipped with dedicated WAGD inlets. Rooms receiving WAGD shall be treated as anesthetizing locations. Contractor shall provide: A dedicated zone valve assembly per NFPA 99 Section 5.1.4.6.2. Area alarm coverage meeting NFPA 99 requirements. INFECTION CONTROL RISK ASSESSMENT (ICRA) Contractor shall coordinate with Infection Prevention and Control and complete an ICRA before work begins. ICRA measures may include barriers, negative air, HEPA filtration, dust containment, restricted work hours, cleaning protocols, and traffic controls. Contractor must implement and maintain all ICRA requirements for the project duration and promptly correct any deficiencies identified by Infection Control, Safety, or the COR. Phasing and Shutdown Requirements Submit a phasing and shutdown plan at least 14 working days prior to any interruption. No room may begin until the previous room is fully commissioned. Each Room Must Follow These Phases: Pre Construction Coordination ICRA Containment Setup Selective Ceiling Demolition & Rough In Gas Shutdowns & Tie Ins. Follow NFPA 99 procedures for tie ins, including depressurization, blow down, leak testing, and post connection re verification. Installation personnel must be credentialed: ASSE 6010 medical gas installers. Brazers qualified per ASME BPVC Section IX / AWS B2.2. Device Installation Ceiling Restoration (hard ceiling rooms only, as applicable in others) NFPA 99 Room Level Testing & Commissioning (CxA witnessed). Room level commissioning includes flow, pressure, cross connection testing, ZVB verification, alarm testing, labeling, and source system checks. Room Closeout & Transition to Next Room Maintain continuous facility operations. Comply with infection control, egress, and safety standards in active care areas. Area Alarm Deficiency: Surgery Ward (Surgery Rooms and Recovery Room) lack any aliquant area alarm. Correction: Provide and install new panels and update existing area alarm to support at the minimum: O , MA, VAC, WAGD, N , and N O. Include all transducers, wiring, labeling, and verification. Provide and install one (1) new Master Area Alarm Panel in Room #3204. New area alarm panel shall support: O , MA, VAC, WAGD, N , and N O. Retrofit the existing hallway area alarm panel and sensors for monitoring rooms #3210 and #3218. Area alarm panel for shall support: O , MA, VAC, and WAGD. Provide one (1) new area alarm panel in the hallway for monitoring rooms #3235 and #3225. New area alarm panel shall support: O , MA, VAC, WAGD, N , and N O. Additional Requirements: All panels shall be fully integrated, tested, and commissioned in accordance with NFPA 99 5.1.11. Dedicated conduit for low-voltage cabling. Supervised loops with proper EOL termination. Panel mounting, programming, and labeling. Relay outputs for BMS / nurse-call integration if required. Sensor commissioning on every monitored line. Full simulated alarm test at each source and each panel. Perform full functional testing, including setpoints, audible/visual alarms, test mode, and signal accuracy checks. Final verification shall be completed by a qualified ASSE 6030 Medical Gas Verifier. Provide a one year warranty on parts, labor, and workmanship. Zone Valve Box (ZVB) Deficiency: Operation Room (PRE OP) and Endoscope lack required intervening walls between ZVBs and the outlets/inlets they serve. Surgery Ward lacks ZVBs....

Track this market for the recompete

This opportunity has closed. Follow NAICS 238220 and we'll alert you when the follow-on contract posts.