Closed
SBA
J012--575 Fire System Inspection & Repairs - one year only
- NAICS
- 561621
- Closed
- Jul 29, 2026
- Posted
- Jun 25, 2026
Description
Q&A Solicitation # 36C25926Q0519 The purpose of this amendment is to: Provide answers to questions received under solicitation 36C25926Q0519. To provide the Joint Commission review tool and clarification document to add awareness for prospective contractors regarding the standards for completing repairs and inspections (see attached). All offers are to be emailed to heather.chase2@va.gov and received no later than 12:00pm (noon) MT on June 29, 2026. Questions and Answers below are referencing RFQ 36C25926Q0519: Q. Will the Government please provide the number of Wet Systems per building? B1: 1 B5: 1 B6: 1 B7: 1 B8: 1 B12: 1 B13: 1 B20: 1 B22: 1 B33: 1 B34: 1 B36: 1 B45: 1 . Q. What is the total number of Dry Systems per building? A. Not in scope of the required repairs. Q. What is the total number of Pre-Action Systems? A. None, station is wet-piped. Q. What is the total number of Deluge Systems? A. Not in scope of required repairs. Q. What is the total number of Backflow Preventers?. A. Not in scope of required repairs. Q. What is the total number of Fire Pumps? A. Not in scope of required repairs. Q. What is the total number of Control Valves? A. Please see CLIN 3 (page 5 & 6) of Attachment 1 - SOW. Q. What is the total number of Flow Switches? A. Please see CLIN 3 (page 5 & 6) of Attachment 1 - SOW. Q. What is the total number of Pressure Regulating Valves PRV? A. Not in scope of required repairs.
Track this market for the recompete
This opportunity has closed. Follow NAICS 561621 and we'll alert you when the follow-on contract posts.